• Welcome to TechPowerUp Forums, Guest! Please check out our forum guidelines for info related to our community.

NZXT E Series 650 W

Joined
Mar 3, 2011
Messages
966 (0.19/day)
Location
Greece
The NZXT E Series 650 W is a modified and slightly more expensive version of the Seasonic SSR-650FX. It features digital monitoring and limited controls, as well as an interesting look. Read the review to figure out whether it is worth spending about $10 more on over Seasonic's offering.

Show full review
 
Last edited by a moderator:
Joined
Jun 1, 2011
Messages
4,679 (0.94/day)
Location
in a van down by the river
Processor faster at instructions than yours
Motherboard more nurturing than yours
Cooling frostier than yours
Memory superior scheduling & haphazardly entry than yours
Video Card(s) better rasterization than yours
Storage more ample than yours
Display(s) increased pixels than yours
Case fancier than yours
Audio Device(s) further audible than yours
Power Supply additional amps x volts than yours
Mouse without as much gnawing as yours
Keyboard less clicky than yours
VR HMD not as odd looking as yours
Software extra mushier than yours
Benchmark Scores up yours
good review, I like the new Component Analysis
 
Joined
Mar 10, 2014
Messages
1,793 (0.45/day)
Good to see Seasonic as OEM. I'm not really fond of those cable capacitors. But this Focus? platform is designed with them on the get-go.
 
Joined
Jun 15, 2015
Messages
33 (0.01/day)
A good PSU ruined by its loudness. Seriously, why does a 650W unit have to be this loud?
 
Joined
Jul 24, 2009
Messages
1,002 (0.18/day)
Good fuse blowing PSU. That inrush is ridiculous.

87A? How much is it in watts? Like 1kW moment you flip PSU on?
 
Joined
Jun 15, 2015
Messages
33 (0.01/day)
120V*87A=10440W=10.4kW.
However only for a very short time, that shouldn't cause a problem.
 
Joined
Mar 10, 2014
Messages
1,793 (0.45/day)
120V*87A=10440W=10.4kW.
However only for a very short time, that shouldn't cause a problem.

It was tested on 230V AC system, so your calculations are bit off.

Don't know how @crmaris is testing that, but ain't it dependable to which part of AC sine wave you actually switch power supply on? Or are these PFC circuits somewhat guaranteeing that switch on is always the same no matter when it's done.
 
Joined
Jul 24, 2009
Messages
1,002 (0.18/day)
120V*87A=10440W=10.4kW.
However only for a very short time, that shouldn't cause a problem.

That would kill even industrial fuse/circuit breaker.

It was tested on 230V AC system, so your calculations are bit off.

Don't know how @crmaris is testing that, but ain't it dependable to which part of AC sine wave you actually switch power supply on? Or are these PFC circuits somewhat guaranteeing that switch on is always the same no matter when it's done.

In case of my PSU which does 66A at switch on, it depends if you 1) switch literally PSU on the back or 2) you have it in power outlet with own switch. Cause in case of 1) my fuses go boom 2) it just works.

Honestly not big fan of high inrush currents. I get that you mostly cant have 30ms hold up without having high inrush (there are some exceptions if Im correct, but very few), but Im perfectly fine if its within regular specs of 17ms and not throwing my circuit breakers.
 
Joined
Mar 3, 2011
Messages
966 (0.19/day)
Location
Greece
High inrush currents are typical, unfortunately, for the majority of PSUs out there. They are very short though and this is why in most cases they don't trip the circuit breakers. There are cases though where I see the online 3kVA UPS, which feeds the AC source, struggling to keep up!
 
Joined
Jul 24, 2009
Messages
1,002 (0.18/day)
High inrush currents are typical, unfortunately, for the majority of PSUs out there. They are very short though and this is why in most cases they don't trip the circuit breakers. There are cases though where I see the online 3kVA UPS, which feeds the AC source, struggling to keep up!

Since you are master of PSUs, any good 1kW (therabouts) PSU that preferably has "gentle" inrush? Or just warning of which ones I should definitely NOT get. :D
 
Joined
Jun 15, 2015
Messages
33 (0.01/day)
There are cases though where I see the online 3kVA UPS, which feeds the AC source, struggling to keep up!

American mains wiring. Its just hilarious.
In most of Europe we use three phase AC, with a regular 63A main fuse that gives one household a maximum power draw of 43.6kVA.
 